8

In my dining room, I would like to install a ceiling light in the center of the room. This room is on the ground floor of a colonial two-story, so there is no attic access into the ceiling; my work space is limited to "within the room itself."

I have an existing switch on the wall, which toggles a wall outlet in the corner of the room. I would like this switch to also control the new ceiling light.

  1. Is it better to branch the electrical wire to the ceiling from the wall outlet, or from the light-switch? Why is one a better option than the other?
  2. How should I go about running the electrical wire to the center of the ceiling, from the corner of the room, with no attic access? Should I cut a long thin strip out of the ceiling and cut a notch out of each crossbeam on the way? Or is there a better strategy?
Tester101
  • 131,561
  • 78
  • 320
  • 610
BTownTKD
  • 183
  • 1
  • 1
  • 6
  • 1
    ...the better strategy would be to run the wire in the wall until you get to a joist bay that lines up with where you want to be in the ceiling - then you don't have to drill any holes in the ceiling joists. – Ecnerwal Aug 20 '14 at 21:32
  • 1
    You should run the cable from the switch (assuming power goes there first), and install a separate switch for the light (either by increasing the size of the box, or by using a double switch). You're going to have to put some holes in the wall, it's unavoidable. – Tester101 Aug 21 '14 at 11:10

4 Answers4

11

The easiest option would be to run a new cable directly from the switch, up to the ceiling fixture. You'll want to either install a larger box and a new switch, or a double switch, so the light can be controlled independently.

Double Switch

If you're working in a home constructed of solid wood framing, you should be able to run the new cable fairly easily. Since you didn't mention where the switch is, or which way the joist run, I'll cover a few scenarios.

Wall adjacent to joists

If the switch is in the middle(ish) of the wall, and the joists are adjacent to the wall. You might get lucky, and simply going up the wall will land you in the proper joist bay.

enter image description here

In this situation, you'll simply have to drill a hole through the top plate, then run your cable.

enter image description here

If you're not so lucky, and the switch box does not line up with the joist bay.

enter image description here

You'll have to bore some holes through the joists to reach the ceiling box.

enter image description here

In this case you'll want to consult local building codes, to figure out where and how to bore the holes.

Wall parallel to joists

If the wall runs parallel to the joists, there's no getting around it, you're going to have to bore through the joists.

In this case it doesn't matter if you're near the middle of the wall, or to one side or the other. The procedure will be the same.

enter image description here enter image description here

enter image description here enter image description here

Boring the holes

To get from the switch box to the ceiling box, you're going to have to drill through at least one structural member. However, if you have the proper tools, the damage can be minimized. To do this with the least amount of damage possible, you're going to want a flexible drill bit, extensions, and an alignment tool.

Flexible Bit Kit

Through the top plate

To drill through the top plate, you'll need to make a hole in the finished wall. Cut a hole in the wall above the switch box, near the ceiling. Cut the hole far enough from the ceiling, so you have room to position the flexible drill bit.

Use the alignment tool to position the bit, and drill up through the top plate. Depending on the construction style, this could be a double top plate.

Through the joists

To get through the joists, you can take advantage of the hole you've cut for the ceiling box. Again use the alignment tool to position the flexible drill bit, and start drilling in a straight(ish) line towards the wall with the switch box. Add extensions as you go, to extend your reach.

Pulling the cable

Now that you have a clear path from the switch box to the ceiling fixture, you'll have to pull the cable through the wall/ceiling. Depending on how things line up, you might have to cut a few hand holes in the finished wall/ceiling to help you maneuver the cable. A fish tape might come in handy.

Future proofing and other considerations

Ceiling fans are a common upgrade, so it might be worth a little added expense now. Installing a braced ceiling box, will allow you to install a ceiling fan in the future.

Ceiling fan bracket

Ceiling fans often come with light kits, and it's common for folks to want to control the fan and light(s) independently. Instead of installing #/2 with ground cable, you might want to install #/3 with ground. This will allow you to install one switch for the fan, and one for the light kit.

Boring vs. Notching

While you may, or may not be able to notch the joists to run the cable. Boring holes can be done with less damage to the finished material, and won't make structural engineers cringe.


WARNINGS:

Consult your local government regarding any permits that might be required. And always follow all manufacturers installations instructions, and all local building codes.

If you're working in a home that does not have solid wood members, consult local building codes for appropriate course of action.

If you try to notch the joist, you could end up with your second floor on your first floor.

Tester101
  • 131,561
  • 78
  • 320
  • 610
  • All good answers, but there are a number of reasons to go with this one. The techniques and tools suggested for boring are much appreciated, as well as the pictures. – BTownTKD Aug 23 '14 at 11:58
  • Could you Amazon link to (or cite product numbers for) those tools? ("you're going to want a flexible drill bit, extensions, and an alignment tool.")? – Scott Prive Jan 14 '19 at 02:23
3

First, never notch the bottom of beams. All electrical runs should be in the center third of any timber. This is for structural support as well as protecting the electrical.

If you want to keep the wall outlet switched, consider knocking out the current one gang and replace with old work two gang. Run a new line up the wall, through the top plate into ceiling joists. You will need to cut at least one access hole into the ceiling to feed cables and then drill through the joists. I would also put a box with enough support to hold a ceiling fan. Since you are adding a box, might as well give yourself future options (also a ceiling fan box will support the heaver lights). If you happen to have a joist right down the middle of the run where you want to mount the light, just use a pancake box and mount to the bottom of the joist.

diceless
  • 4,416
  • 1
  • 17
  • 18
  • 1
    I about had a kitten at the thought of notching those timbers... ESPECIALLY the BOTTOM edge, where all the tensile strength comes from. – TDHofstetter Aug 21 '14 at 00:19
  • 1
    If you're looking for future expansion, run #/3 with ground cable from the switch to the fixture. Then if you do install a ceiling fan with lights, you can control the fan and lights independently. – Tester101 Aug 21 '14 at 10:48
  • 1
    I've never seen a building code that had a problem with notching joists, as long as it's within specific limits. IRC specifies no notches in the middle 1/3 of the span, a maximum notch depth of 1/6th the "depth" of the member, and a notch length 1/3 the "depth" of the member ("depth" being the height of a joist). e.g. a 2x10x18 can have notches anywhere within 6' of the ends, with a maximum notch length of 3" and depth of 1.5". See this answer for more information. – Tester101 Aug 21 '14 at 11:03
  • 2
    However, if you do run electrical cable through a notch, you must protect the cable from physical damage using a steel plate or equivalent. – Tester101 Aug 21 '14 at 11:05
  • Do you know how they define "at the ends of the members"? That appears to be distinct from the 1/3-1/3-1/3 specification. I ask because "The tension side of members 4 inches (102 mm) or greater in nominal thickness shall not be notched except at the ends of the members.". From an engineering standpoint, notches in the bottom (tension) edge of a joist are a nightmare because they significantly reduce the rigidity & ultimate strength of the joist. – TDHofstetter Aug 21 '14 at 12:43
  • @Tester101 How did you determine the floor is supported with sawn lumber and not an engineered system of joists and beams? –  Aug 21 '14 at 12:46
  • @benrudgers How did you determine it's not? – Tester101 Aug 21 '14 at 12:56
  • @TDHofstetter "at the ends of the members" means the portion of the beam that is over the supporting member. For example, you can notch the joist so that the supporting member fits into the notch (take a look at the diagram labeled "Floor Joist -- End Cuts", notice how on the left, the joist is notched to fit the support member). – Tester101 Aug 21 '14 at 13:04
  • Do we know that this house isn't timberframe or transitional? What ARE the thicknesses of the joists? – TDHofstetter Aug 21 '14 at 13:19
  • @Tester101 I did not make a determination one way or the other. I did not imply to a person without a background in construction that having a go at it with the sawzall was a reasonable course of action, either. This is because my professional experience has taught me that when faced with the unknown not to trust what I imagine to be the case but to instead attempt to systematically consider what could be the case and to proceed in way consistent with the knowledge that I don't have all the relevant details. Despite owning a sawzall. –  Aug 21 '14 at 13:36
  • @benrudgers First of all, I never mentioned the use of a sawzall (reciprocating saw) to notch joists. Secondly I said "I've never seen a building code that had a problem with notching joists, as long as it's within specific limits.". I then went on to explain some of the limits, and included a link to a more detailed explanation. "never notch the bottom of beams", and "All electrical runs should be in the center third of any timber." are simply not true, and I'm trying to explain why in my comment. – Tester101 Aug 21 '14 at 13:45
  • @Tester101 This ain't paint. It's life safety. The building code has a big problem with notching and drilling Wood framed structural members shall not be drilled, notched, or altered in any manner except as provided in this code. [IRC 2006.E3302] The starting point is notching is prohibited. It is incumbent upon the person with the sawzall to demonstrate that all the criteria for an exception have been met before they pull the trigger. Language matters. A floor truss is not a joist. An I-Joist is not sawn lumber. A glu-lam has to be treated differently. –  Aug 21 '14 at 14:04
  • @benrudgers Which is why I linked to the building code, and provided the information as a *Comment* not an Answer. I'm simply pointing out that it is possible to notch joists, in some situations. I'm not advocating notching joists, just pointing out that they may be a valid option. – Tester101 Aug 21 '14 at 14:45
  • 2
    @Tester101 The question indicated an awareness that structural members can be cut. What was not indicated was an awareness of code requirements and experience and training necessary to properly interpret and implement those requirements during construction. The comment would be fine for the audience at MikeHolt's because those people typically own and frequently read and apply the relevant codes...from experience they know what sort of mistakes they make. In my opinion, it is an error of judgement to assume that people out side the industry are similarly informed by experience. –  Aug 21 '14 at 15:47
  • @benrudgers I agree that not everybody should be doing their own construction work. That's why when I answer questions I try to explain things further, provide drawings, examples, and warnings, rather than simply answering the question. I'm also not afraid to suggest somebody seek professional help, when I feel they are in over their heads. – Tester101 Aug 21 '14 at 16:01
1

Depending on the condition of the floor above your ceiling, it might be easier and cheaper to access the ceiling void through the floor. For example, if the floor upstairs is going to be renovated too, or if the floor cover is a carpet, which can be lifted and put back easily, or even better - if it is just the original floorboards, you can easily lift one or two floorboards. They run at a right angle to the joists, so you will have access to all the joists you need to drill through. In all the houses I have done this, the ceilings were plasterboard, so going through the floor was the obvious option.

Check the electrical installation regulations for residential properties in your country/state/whatever. In UK unprotected cables in the ceiling void should be at least 50 mm below the floorboards. And some electrical works are notifiable - you are supposed to inform your local council before you start them, so they can provide the necessary control (and get your money). So check the technical and the legal regulations if you are not sure.

greenfingers
  • 131
  • 2
0

Just to point out the other solution: Any the new fixture as a swag lamp, surface-mounted with a decorative treatment bringing the power cord across the ceiling and down to an outlet. That's how my living room is currently lit.

Or do a fake coffered/beamed ceiling, running the wire through the "beams".

keshlam