I have a new 15amp circuit with AFCI breakers. It is dedicated for 120v electric fireplace. The issue I am facing is that the moment I turn the fireplace on the breaker trips. My questions are -

  1. Shall I replace AFCI with a regular 15amp breaker?
  2. Shall I replace the regular receptacle with an AFCI receptacle and afci breaker with regular breaker and still maintain the security of orginal AFCI breaker?

Thanks, looking forward to all the suggestions.

  • 1
    AFCI looks for sparks/arcs in the wiring. Should not have any with electric fireplace, maybe a gas one with an igniter. I would check the fireplace and the wiring first, then maybe think of changing with the breaker/outlets. – crip659 Jan 05 '24 at 20:44
  • 2
    When a breaker trips (any type of breaker, for any reason) your first thought should be "there's a wiring problem", not "my breaker is bad". Did you have a licensed electrician install the circuit? If so, call her back and ask her to trouble shoot. Also, do the fireplace instructions say it's compatible with AFCI protection? – FreeMan Jan 05 '24 at 20:52
  • 1
    The AFCI might be a red herring. A breaker tripping as soon as a switch is turned on, usually is a short on the switch hot wire, usually in the switch box. A screw or ground wire too close. – crip659 Jan 05 '24 at 21:23