Goal: I’m installing a 400 Amp service in Washington State through Mason County PUD 3. The AHJ is Washington State L&I. For now, I’m installing what’s necessary to power my RV and well pump but I want the service entrance to be done in anticipation of 200A for my Shop/ADU/RV and 200A for my house, to be built in 1-2 years. Before I go asking stupid questions to L&I, I wanted to run my plan by you wise people.
Electrical experience: Not zero, but pretty close.
Q: Does this plan and shopping list sound reasonable and up to code: One in-ground run 750-750-500 MCM Aluminum XHHW-2 from transformer 170ft to meter, in 4” schedule 40 @ 18.96% fill. Replace 600 MCM meter socket line side lugs to accept 750 MCM. 200A panel w/ disconnect, 100A fuse for 100A sub panel, 30A fuse for well pump and one 110 outlet. Ground panels with 2/0 CU. In-ground run of 1/0-1/0-#2 AWG AL XHHW-2 175ft to 100A sub panel for RV (has 50A, 30A, and 20A fuses). Use 1.5” sched. 40 @ 21.09% fill. Ground with #6 CU.
Shopping list:
Eaton B-Line 400A, 4P, 4 Jaw, Ring-Type Meter Socket (already purchased)
750 MCM AL XHHW-2 x 360ft = $1199
500 MCM AL XHHW x 180ft = $407
4” sched. 40 x 140ft = $1200
4” sched. 80 x40 = $32
Lug kit = $128
2/0 awg CU THWN-2 for groundx 10ft = $32
Square D Homeline 200 Amp Outdoor Main Breaker = $235
For 100amp RV subpanel 1/0-1/0-#2:
1/0 AWG AL XHHW-2 x 360ft = $227
#2 AWG AL XHHW-2 x 180 = $74
1.5” sched. 40 x 180ft = $418
Total= = $3952