I have a 1961, Apartment with Bolted on panels vrs the Stab-lock is bolted on safer?
Asked
Active
Viewed 75 times
0
-
3You have two identical questions, please delete one. Not clear what you are asking. Stablok is a brand with known problems. Bolted on is a technical yen that can apply to many brands. What do you actually have? Pictures would help. – manassehkatz-Moving 2 Codidact Dec 14 '23 at 18:26
-
2If this is an apartment, as in a rental, there's nothing you can or should legally be doing in the panel anyway. – FreeMan Dec 14 '23 at 19:13
-
1Good read: https://diy.stackexchange.com/questions/62320/should-all-federal-pacific-panels-be-replaced – nobody Dec 14 '23 at 19:34
1 Answers
4
If you are talking about Federal Pacific Electric in both cases (bolt-on and snap-in, both exist under the "Stab-Lok" name), the whole thing needs to be replaced promptly either way. The internal mechanism has several problems according to http://fpe-info.org/hazardous_fpe_171110.pdf which has nothing to do with the bus connection method:
- Breakers often don't trip at their rated current, but at a much higher level, which can lead to fires
- Breakers can jam on overcurrent and not trip at all, which can lead to fires
- Breakers can jam when manually moved to "off" which is a safety problem and also possible fire hazard
Some (probably not all) of the bus-connection problems may be mitigated by the bolt-down breakers, but that does not make them acceptably safe. Either way, these panels are a fire hazard and need to be replaced promptly.
nobody
- 6,670
- 3
- 31