Initial state: two BX (old metallic-sheathed cable) arrived at one outlet box on the second floor. They are sourced from a pair of 15 amp breakers tied together as an MWBC at the panel. Apparently, they show up at the panel with just one neutral, even though they arrived at this box with distinct neutrals. There is probably a junction somewhere in between. (Professionals did the panel for me last year.) It was a frighteningly crowded box, with an outlet.

Exiting the boxes was knob and tube up to junction boxes in attic. Out of the junction boxes came a mixture of knob and tube and modern NM, feeding a mixture of plugs and lights. Yea, welcome to 1920, as gradually modified since.

I got to see and change this when we gutted a bathroom on the second floor which exposed the back of this box.

(We got an clean NM circuit for the plugs in the refurbished bathroom. I was not prepared to rewire the whole house or get new home runs in place of the BX. It would take up too much room to explain why it was feasible to fix the outlets.)

I split the box into two boxes. I replaced the runs of K&T up to the attic with NM. Each box ended up with one BX coming in, one NM going out, and an AFCI outlet in the middle. Why two boxes and not one big one? I could avoid disturbing the intact lathe and plaster around the original box and open the new box into the bathroom vanity cabinet.

I neatened up the junction boxes in the attic so that the remaining K&T was handled appropriately. I did all this work while the walls were open in the bathroom. For 'reasons,' it took weeks for all the finish to get done. Nothing went wrong during this time, with power flowing through the AFCIs to the legacy wiring, including to one laser printer and one microwave oven.

Then, we finally were ready to turn on the new bathroom lights, which were wired downstream of one of the AFCIs. (In perfect 20-20 hindsight, I realize that for a little more wire I could have tied them in upstream. Since I knew that there was a mixture of lights and plugs downstream that I could not sort out, I didn't bother.)

We turned on the lights. All was well. Then the laser printer came on. The AFCI tripped. Note that it did not trip when the laser printer ran before we connected and turned on the lights. Remembering a prior saga with a laser printer and a GFCI, I move the printer to another part of the house that has modern wiring, and all was well. The next morning, someone turned on the microwave while the bathroom lights were on, and the AFCI tripped again.

For now I've taken out the AFCI on this branch.

By working down from above, I could still rework this to get the bathroom lights upstream of the AFCI. Still, I would still like to have some clue as to exactly what is going on here. The bathroom light fixtures are LED, they should not draw much current. Why does the combination of them with an inductive load trip the AFCI?

I could also prepare a big surprise for the next owner of this house by putting one or more AFCIs up in the attic so each one handles a smaller and better understood set of wiring. 'surprise' because, if one ever trips, no one is going to guess that there is a box-o-AFCI's in the attic.

Reading some other questions and answers, I suspect that the response here will be to go on a hunt for crossed neutrals downstream from here. I have corrected a fair number of bootlegged grounds, but I guess it's possible that I missed one, as well. Answerers are free to vote to close as a duplication failing any unique ideas about this particular story.

bmargulies
  • 385
  • 1
  • 3
  • 18
  • 1
    AFCIs trip on arcs/sparks. Could one of the connections be loose(causing a spark)? – crip659 Nov 19 '23 at 22:23
  • 2
    @crip659 And in particular, both the laser printer and the microwave oven use a lot of power (often 1000W or more) so they could expose a weak connection that wouldn't arc enough from a few W of lights. – manassehkatz-Moving 2 Codidact Nov 19 '23 at 22:31
  • 1
    OK, I get that. But if that were the issue, I wouldn't expect the bathroom lights to make any difference. The microwave and the laster printer were chugging along downsteam from the AFCI for several weeks without any trips. – bmargulies Nov 19 '23 at 22:51
  • 2
    So, if there's a loose connection in the new lighting, the laser printer or the microwave could manage to trigger an arc in there? – bmargulies Nov 19 '23 at 22:54
  • Are these BX cables "old style" cables that just have the two wires in paper packing and metal armor, or the newer type AC cables that have a thin aluminum bonding wire just beneath the armor? Also, I take it we're talking about receptacle-style (Outlet Branch Circuit) AFCIs here, not AFCI breakers in a panel? – ThreePhaseEel Nov 20 '23 at 02:18
  • Yes, what's what I learned to call BX in my youth. Yes, AFCI outlet, not breaker. – bmargulies Nov 20 '23 at 20:03
  • The only way you should really run an AFCI on a MWBC is to use a dual-pole breaker. I'm confused why you're expecting to see two neutrals at the panel. the whole point of a MWBC is to only have one neutral for two circuits. trying to use an AFCI receptable inline on only one leg of the MWBC seems like it's just asking for trouble... – ickybus Nov 20 '23 at 20:21
  • There are two neutrals in the bathroom in cables that do not have that far to run to the panel. So, really, I am puzzled as to how they end arriving at the panel as one neutral. I see your point about ignoring the MWBC just because I have a neutral here. – bmargulies Nov 21 '23 at 00:54
  • In a couple of weeks I may get an opportunity to learn more about the other end of these cables as we work to recover cold water to the kitchen -- a whole other related saga. – bmargulies Nov 21 '23 at 00:59
  • @bmargulies -- it sounds like there's a MWBC homerun from the panel that splits into its component circuits before it reaches where you're working – ThreePhaseEel Nov 21 '23 at 03:53
  • @bmargulies -- also, what make/model OBC AFCIs are you using? – ThreePhaseEel Nov 21 '23 at 03:53
  • I am a thousand miles away from it at the moment, but I think they are leviton. – bmargulies Nov 22 '23 at 14:57