0

Can I put seven 12/2 cables in one 4 x 4 x 2-1/8 square metal junction box? According to some box fill calculators, this may be a tad too many wires for this junction box. However, I'm hoping I'm wrong. Other wise I may have to use two junction boxes.

Adding context: This junction box will serve 4 new closet lights and new light switches, along with an existing bathroom vanity light and switch and 4 existing recessed led lights (on one switch). Along with the power source line in, it is a total of seven 12/2 cables.

navig8tr
  • 145
  • 6

1 Answers1

4

12 AWG = 2.25" x 15 (14 conductors plus 1 for all the grounds) = 33.75"

In NEC 2020 (not adopted everywhere yet), every 4 grounds count as 1:

12 AWG = 2.25" x 16 (14 conductors plus 2 for all the grounds) = 36.00"

4" square 2.125" deep box I found listed as 30.3", which is less than 33.75". So it won't work.

Add a domed cover for another 7", total 37.3", and you are OK even with NEC 2020.

You can also use a 4.6875" (4-11/16") x 2.125" box sized at 42". That gives you room to spare - enough for one more cable.

I found a great PDF of box dimensions - not everything listed on Home Depot or other retail sites includes cubic inches.

manassehkatz-Moving 2 Codidact
  • 115,769
  • 11
  • 130
  • 326