I am going to be installing a subpanel in an unfinished detached garage, and would like to install receptacles in each corner of the building.

Since the garage is unfinished (cinderblock walls), I'm going to place all of the cable ( as Romex) in Schedule 40 PVC conduit for the vertical runs from the receptacles to the rafters. To run the Romex between the building corners, I plan to run it stapled across the rafters more than 7 feet up.

At the top of each vertical conduit run, do I have to install a terminal adapter the end of the conduit electrical box & splice it to a Romex that's clamped to the box? Or is there some kind of bushing or strain relief connector that I can use on the end of the conduit, so the same piece of Romex can be run from one corner to the next?

Ecnerwal
  • 213,340
  • 10
  • 261
  • 571
Bob
  • 45
  • 5
  • Not an exact duplicate but see https://diy.stackexchange.com/questions/31149/can-romex-nm-b-cable-be-run-through-conduit – whatsisname Aug 29 '22 at 06:45
  • What kind of "terminal adapter" are you thinking of? You may want to include a picture or at least a link to one. – FreeMan Aug 29 '22 at 11:49
  • 1
    With intact NM cable inside PVC conduit why do you need to do anything? Just staple the cable near to where it exits the conduit. The conduit protects the cable at lower levels, the plastic conduit end is not damaging to the plastic outer jacket of the cable, and the cable is appropriately fastened by staples to the ceiling. Why add complexity? – jay613 Aug 29 '22 at 14:16
  • @jay613, I would tend to accept that myself, but I just want to insure that it's acceptable to the electrical inspector. As I'm a DIYer, I didn't know if there were any restrictions via NEC. – Bob Aug 29 '22 at 14:21

1 Answers1

3

You can get a female adapter like this enter image description here

and attach it to your PVC and then screw this adapter into it after removing the lock nut (Stock photos from home Depot). You can also add a PVC 90 degree sweep in the direction of the run if neatness counts.

enter image description here

JACK
  • 80,300
  • 19
  • 72
  • 190
  • 1
    @Ecnerwal Thanks... need more coffee – JACK Aug 29 '22 at 13:32
  • Thanks, @Jack. That sounds like it'll work. Hopefully the inspector will accept it. – Bob Aug 29 '22 at 14:06
  • Why don't you try one of these and one with a bare conduit end and see if the inspector accepts either or both. I think this would be my preferred solution if the cable were exiting the conduit into, say, a suspended ceiling where I'm fishing it further and unable to fasten it to anything. But if you're stapling at the transition, IMO either way is OK and either way equally likely to irk an inspector for no good reason. – jay613 Aug 29 '22 at 15:01