0

In a main panel I know if you use too much power at once you can over load the main panel, but I was wanted to know if the breaker in a main panel that you would use for a sub panel if it could be overloaded due to the other breakers in the main panel using power at the same time as sub panel, which makes you use more power then the main panel is rated for.

I guess I’m really just trying to ask if the sub panel is making the main panel have to use less power or does the power that the sub panel use not effect any breakers in the main panel.

For example if my main panel needs more breakers and is overloaded, would a sub panel solve the problem or is a sub just to split the breakers into different sections while using the same amount of power.

Thanks for any answers it will help a lot.

Miller
  • 1

2 Answers2

3

"Stealing" is odd terminology. It's perfectly legitimate use.

All the power for a subpanel is part of the power that flows through the main panel that feeds it. Subpanels provide more spaces for breakers, not more total capacity.

So, if your service is overloaded and the main breaker is tripping, you need a service upgrade, not a subpanel. Your existing main panel might become a subpanel in the new scheme.

Also, if your main is tripping, there might very well be some accumulated electrical code violations going on, since a fully-code compliant installation is sized in such a way that that does not happen from normal use. So you might want to look very carefully at the whole electrical system for possible shoddy work carried out after the initial installation. i.e. if the house was built with a gas range (and/or dryer) and someone swapped it out for an electric range without making sure that the total service load was within bounds after that Very Large Addition, it wasn't done correctly...

Ecnerwal
  • 213,340
  • 10
  • 261
  • 571
  • Thank you, and I’m going to replace the main panel, and the rest of the wiring in the houseI just wanted to know so I can calculate my load correctly, also I have noticed a lot of code violations like the fridge is on the same circuit as a few kitchen outlets and light fixtures – Miller Jun 06 '22 at 02:21
  • Whether that's a code violation depends on where you are. In the NEC, it's not (the lights sharing it are, I think). Apparently it might be under the CEC. I prefer the dedicated fridge (or fridge & freezer) circuit myself, but it's not required by unmodified NEC code. – Ecnerwal Jun 06 '22 at 02:28
  • 3
    Depending what, exactly, you currently have for panels and wiring, that might be a long overdue very good idea, (FPE Stablok, disintegrating cloth insulated wires) or a complete waste of money (many but not all other makes of panels, "old" plastic-insulated wire that's not damaged and good for another 50 years...) - you might want to frame some new questions with detailed pictures of what you've got for input before jumping that direction. – Ecnerwal Jun 06 '22 at 02:45
  • 1
    Incidentally, a load calculation is a specific procedure, not "add up the numbers on all the breakers and flip out" since it's not uncommon for the breakers in a panel to add up to much more than the main, while the load calculation is safely below it. e.g https://diy.stackexchange.com/q/195393/18078 – Ecnerwal Jun 06 '22 at 02:48
3

Every load takes the power that it wants to take.

That is decided by you switching it on. If you run a dryer load, the dryer is going to take 5500 VA give or take.

VA = Volts x Amps, similar to Watts. It is a rate of flow of energy. When we think about overloading panels, this is the usual figure that is used. It is simplest, and avoids 120/240V complications.

When the water heater cycles on, it takes 4500 VA when it's on.

Take the breaker on your main panel, multiply by 240V. If it's 100 A, then that's 24,000 VA. Get it? Don't plan to exceed 80% of that.

If you have a subpanel, that works the same way - multiply the breaker amps x 240V = rating VA, then multiply by 80% (0.8) for the limit of what you can plan to use.

Now, if you've been following along, you may notice both your dryer and water heater have 30 amp breakers. Yet one is 5500 VA and the other is 4500 VA. Yes, the breaker does not indicate the power the device takes! The device does. Each device will have a nameplate which states that, either in volts and amps, or VA, or watts.

The panel doesn't have any way to slow down the power.

Whatever your loads draw, that rolls right through the panels. There is nothing in the panel that will limit current.

Except for the circuit breaker, of course. But you're not allowed to plan to use more than 80% of breaker trip, as said.

The breaker has is highly forgiving and will allow short term overloads. (e.g. to allow motors to start up).

Load Calculation

If you are studying whether the main panel or subpanel is big enough for its loads, then you do a Load Calculation, which is a procedure described by NEC Article 220, and documented many places. It uses the "VA" figure. The Load Calculation uses some "catch-all" figures which cover almost all 120V loads, so you don't have to count them for the most part.

All the loads in the house come through the main panel. If a load comes out of a subpanel, then the power flows through both the main panel and the subpanel. It's possible to chain subpanels, of course.

When you do a Load Calculation, you figure for all the loads fed by that panel. Including loads that come through a panel to another panel.

Number of breakers in the panel has nothing to do with it.

Lots of people have panels that are full, because someone in the past decided to save a few dollars by skimping on breaker spaces. I sure hope they enjoyed that pizza.

The number of spaces in use doesn't have all that much to do with whether the panel is overloaded. The Load Calculation tells you the facts there.

Harper - Reinstate Monica
  • 300,628
  • 26
  • 286
  • 734