5

So in the place I'm currently staying, they use an inline hot water heater1. This is a ~5500W, 50A beast2 that replaces the shower head and heats up the water as it comes out. Notably, even 5500W isn't enough to really get the water hot if the flow rate is high, but it's certainly better than nothing.

I noticed that when I turn the water on, the bulb in the bathroom gets brighter. That's the opposite of what I would have normally expected. I whipped out the multimeter, and sure enough when the shower isn't running, I am reading 92V-95V3, but as soon as I turn it on and the shower starts drawing ~30A, the voltage increases to about 107V, which explains the brighter bulbs.

I'm used to a heavy load like a 30A4 either dropping the voltage, on a system with long insufficiently thick wiring runs (or a weak voltage source, like a generator or inverter near its maximum load), or holding steady (a well designed system) - but what could cause a load to significantly increase the system voltage?

Notes: I wasn't able to measure the voltage at the shower head itself - I measure it at an outlet elsewhere in the house. You can't see it in the picture, but the ground wire which comes out of the back of the shower head is simply pigtailed to neutral, which is why you only see two wires coming out of the head - unsafe as hell, but could this also have an effect, e.g., by providing a second return path for current?

Inline Hot Water Heater


1Admittedly, I'm just making this name up - I'm sure the correct term is lurking out there somewhere.

2I've never seen these in Canada, the US or Western Europe, so I'm kind of guessing they are against code. Having live mains voltage in your shower doesn't seem like a great idea, and many that I've seen have bare copper exposed on the hot wire, so you are just a couple inches away from a bad accident when you reach up to adjust it. That said, they are very common at least across Mexico and Guatemala, where plumbing is either absent or cold only. Dual hot/cold plumbing is very rare.

3Yeah, it's out of spec, but this is rural Guatemala we are talking about.

4It's on full, so it should be trying to draw 50A, not 30A, but it's probably experiencing a lot of voltage drop on the long wiring run to the shower head.

BeeOnRope
  • 181
  • 7
  • What is the voltage? I haven't seen a 120v model that large but if it is an imbalance on 1 leg can cause the other leg voltage to increase. If 240v I haven't seen a heavy load cause an increase in voltage. – Ed Beal Oct 06 '16 at 17:17
  • @EdBeal - close inspection of the photo shows that the device is a 120v unit. So you're certainly correct that it's causing an unbalance - not all that surprising at 5kW. – brhans Oct 06 '16 at 17:23
  • Yeah it's a 120V unit. Can you give some details about a possible imbalance and how I could measure or confirm it? I should note my voltage readings were from hot to neutral. – BeeOnRope Oct 06 '16 at 17:50
  • FWIW the unit is about the same size as many of the other's I've seen. I think the way I took the picture makes it seem bigger. It's only about as big as your hand, top to bottom. – BeeOnRope Oct 06 '16 at 17:52
  • Is the service imbalanced where it enters the house building? Is it a split phase type service like USA? What is the spec voltage in Guatamala? Or only when measured at the remote point within? A loose (or high resistance) neutral connection especially that is common to both circuits tested could cause readngs such as yours. – Tyson Oct 06 '16 at 19:16
  • Is the outlet on the same leg as the heater, or the opposite leg? – ThreePhaseEel Oct 07 '16 at 02:13
  • @Tyson - I can't really tell. I can't assume it's wired in a reasonable way as most of the work here is done in an ad-hoc way, often by people without formal training. I can see a hole in the wall where the service enters and it passes into a two-breaker both (30A and 40A), but I'm not sure what more I can determine for that. Guatemala is a ~120V nominal country like the US and Canada, but I'm not sure what the exact spec voltage is. Most places seem to run about 110V. – BeeOnRope Oct 14 '16 at 22:24
  • 1
    @ThreePhaseEel - good question. I can try to find out by flipping the breakers on and off (it's not clear if this place has multiple legs, but it seems like yes). – BeeOnRope Oct 14 '16 at 22:24

2 Answers2

1

This seems like the neutral cable in a split 120-N-120 service is not handling the full current. A small gain in brightness of a lamp on one side of the circuit, when a 30 or 50 A load is applied to the other side, is not unusual, but measure the voltage if it's more than a barely-noticeable increase in brightness. The maximum voltage should be no more than ~127 V.

In the extreme case of a neutral wire breaking (which happened to my service after a tree fell on the entrance cable), the voltage across each half of the circuit becomes 240V split by the resistance for the circuit. E.G. with a 40 A designed load (3 ohms) on one side, and a 1 A designed load (just a 120 W lamp, 120 ohms) on the other side, the actual voltage across the lamp would be ~234 V, and the 40 A water heater would get only ~6V. The lamp would be very bright for a very short while. (In my case, I was lucky -- a few lamp ballasts burned out, but over-voltage protection varistors on outlets blew circuit breakers before a fire started).

DrMoishe Pippik
  • 7,349
  • 16
  • 26
  • The brightness increase is significant, and as noted above it's about a 12 to 15V change, from ~92V to ~107V. – BeeOnRope Oct 14 '16 at 22:26
  • What I don't understand is how you get 240V across an outlet on one leg in the scenario that the neutral breaks? Wouldn't this just break the circuit? Where does the connection to the other 120V leg come from? – BeeOnRope Oct 14 '16 at 22:29
  • 1
    @BeeOnRope -- from one hot to the other hot via the house neutral system. – ThreePhaseEel Oct 14 '16 at 22:53
  • 12 - 15 V is a bit more of a swing than desirable. It indicates the neutral line from the entrance panel to the transformer is not handling the current. Since it's not your own home, you might suggest to the owner that he have an electrician check out the issue. There is some danger of the wiring overheating, or of losing the neutral and then having ~220 V on the opposite circuit from the heater. – DrMoishe Pippik Oct 16 '16 at 02:54
0

If I would have done the math 5500/120 = 45.8 amps. To verify it is a load imbalance causing the problem an amp clamp meter will be needed. You may be able to move breakers around to balance the load on the service. With one leg heavily loaded and the other not loaded an increase in the voltage on the unloaded side is not unusual. Code requires balanced loads but gives no specific percentage that is allowable. This may be almost impossible to fully balance but moving more of the 120v loads that may be in use while the water heater is running will reduce the imbalance and reduce the voltage swing you are observing. I would only try to reduce the imbalance because after the water heater is turned off the imbalance will be on the other leg.

Ed Beal
  • 102,735
  • 4
  • 75
  • 155
  • I have a clamp meter, which is how I measured the 30A flow. There are only two breakers total at the service entrance, so I can't really move anything around. Partly it was more curiosity about how this could occur. – BeeOnRope Oct 14 '16 at 22:27