Questions tagged [gfci]

Ground Fault Circuit Interrupter(GFCI). Sometimes known as a GFI, or a residual-current device (RCD or RCCB). Can refer to receptacles as well as circuit breakers. They detect a leak in current, or an imbalance between the current on the hot and neutral wires. This is used to prevent electrical shock. Use with the [electrical] tag

Ground Fault Circuit Interrupter(GFCI) devices are usually required where electricity can contact water or some other ground, including kitchens, bathrooms, and outdoors. They work by detecting an imbalance (usually around 5mA) between the draw on the hot and the returning current in the neutral, and thus will disconnect(interrupt) the circuit. This prevents electrical shock. GFCI receptacles can protect down-circuit receptacles, provided those outlets are attached to the LOAD side of the GFCI.

The breakers may be installed within the breaker panel or as a receptacle or stand-alone, "dead-front" device in North America; they are typically found in the breaker panel in other parts of the world. In Europe, these may be called a Residual Current Device(RCD, usually for receptacles) or a Residual Current Circuit Breaker(RCCB), but they work the same way.

Similar to (but not the same as) Arc Fault Circuit Interrupters(), which are used to protect against arcing that could cause a fire. Some circuit breakers will do both GFCI and AFCI.

1271 questions
10
votes
2 answers

Why is an inoperative garage outlet labeled "GFCI protected" not a GFCI?

I have a 25 year old home in Arizona. The breaker panel is standard with no GFCI circuits. I have 4 outlets in the house/garage and one outside, that do not work and people tell me that is because the GFCI in the garage was tripped. There are no…
9
votes
6 answers

Must outdoor GFCI power outlets be covered?

I have outside the regular (i.e. non-GFCI) power outlet that you see on the left. It has a nice double-cover that will keep water out. I am about to replace it with a GFCI outlet (right of the picture). The GFCI outlet will not accept the…
Calaf
  • 1,225
  • 7
  • 25
  • 47
7
votes
2 answers

Can I install a GFCI outlet downstream of another GFCI outlet?

I have a circuit protected by a GFC breaker and I change a regular receptacle with a GFCI receptacle and now same time I have a trip breaker, is ok or not to do this??? Details: Main GFC breaker is for a sunhouse and the GFCI receptacle is daisy…
6
votes
4 answers

Does a GFCI receptacle provide overcurrent protection?

Does a GFCI receptacle provide over-current protection? (note that I'm not referring to GFCI circuit breakers as may be found in a service panel, nor to specialty devices such as an inline plug-in GFCI that may offer over-current protection) I've…
Johnny
  • 4,855
  • 9
  • 28
  • 36
6
votes
6 answers

Can I plug a multi-outlet adapter into a GFCI outlet?

I have a GFCI outlet in my kitchen where I would like to plug in more than two things. I was thinking I could just add a multi-outlet adapter to one of the outlets, or maybe a short 1->3 plug extension cord for my purposes. I'm assuming this is…
Peter Tirrell
  • 421
  • 3
  • 6
  • 15
6
votes
3 answers

New GFCI outlet popping with high powered appliances

When I plug a high powered (1200W) device into my new GFCI outlet the GF circuit pops after 3 or 4 minutes. It does not pop if I plug the same device into a downstream outlet fed by the load terminals. It does not pop with smaller devices. This…
jay613
  • 37,422
  • 2
  • 51
  • 148
6
votes
2 answers

Can both line and load go to same screw on a GFCI outlet?

I was going to replace my GFCI since it is not working. The GFCI has 2 black wires going into the same screw -- one with the push in connection and the another wired to the screw. Same for the white. My guess is that one black wire is for load and…
5
votes
3 answers

Why would the neutral wire in my bathroom's outlet box have voltage?

My wife was using the hair dryer in the bathroom, connected to the GFCI plug when the power to the bathroom plug went out. I toggled the circuit breaker on/off, still no power. Suspecting the GFCI outlet is bad, I replaced it with a new one, and…
MazDama
  • 51
  • 1
  • 1
  • 3
4
votes
2 answers

GFCI is popping for no reason

This morning we woke up to the bathroom lights not working. Investigation reveals that the culprit is the GFCI that serves two bathrooms and the laundry room. It still pops in 10-15 seconds with no draw whatsoever on anything that appears to be…
Loren Pechtel
  • 974
  • 1
  • 7
  • 14
4
votes
4 answers

Why are GFCI systems typically in the receptacle instead of in the breaker?

Since the breaker box contains all the other electrical safety equipment it would make sense to put GFCI systems here; and GFCI circuit breakers are available which do this. But GFCIs inside receptacles are much more common. Is it just because…
Billy ONeal
  • 727
  • 2
  • 9
  • 18
4
votes
3 answers

How to install a GFCI?

I would like to replace a regular plug with a GFCI plug. The current plug has: Ground (green in picture) White Black Red (connected on the same side than the Black with broken tap) The breaker is "double" (see picture) To the best of my knowledge,…
collifu
  • 43
  • 3
3
votes
2 answers

GFCI Outlet wired to non GFCI. Can I switch?

I have a GFCI outlet that is wired to another non GfCI outlet. So when either has a problem, they will trip off. My question. Can I reverse these outlets? Let's say the GFCI outlet is on my left and the non-GFCI outlet is on my right, can I…
Roy Barr
  • 31
  • 1
  • 3
3
votes
1 answer

Appliances plugged in GFCI outlet works but when plugging in the downstream outlet doesn’t

When I plugging coffee machine in the GFCI outlet, it works but does not in the downstream outlets. The Voltage of downstream outlet drops to 87V after plugging in the downstream outlet.And shows open neutral if plugging tester. GFCI wasn’t tripped…
Joe
  • 31
  • 1
3
votes
2 answers

Understanding GFCI configuration in basement

Good day- I am putting a treadmill in the basement of our three-year old home, and the manufacturer warns not to plug the treadmill into a GFCI outlet. Although the outlet I anticipate using is not itself GFCI, I assume it is downstream from the…
Andrew
  • 31
  • 1
  • 3
3
votes
1 answer

Why don't downstream outlets work after replacing a GFCI outlet?

I have a GFCI receptacle in the garage. There are two regular outlets in the garage as well that I believe are "downstream"/protected by this outlet as required by code. There is also another regular outlet on the circuit that is inside in the…
cathy
  • 31
  • 1
  • 2
1
2 3