1

So this is still not very clear to me: I am trying to get 240V to an appliance that does not need a plug (direct wiring), I won't need a neutral wire, is this right? In fact there is nowhere to connect it on the appliance, right? I just need the two hot wires wired to the L1 and L2 lines and it will work. Additionally, I can wire the ground to the ground line, for safety (not doing this would be crazy), but no current would go through this during normal operation, right? I might be completely wrong here, just trying to understand.

I started from this thread: Why Do 240V Circuits Not Require Neutral?

MANY
  • 13
  • 1
  • 1
  • 3

3 Answers3

3

Depends partly on the device. Some electric ranges/cooktops/driers have electronic controls which run on 120V even though they're controlling 240V; they get that 120V by connecting between one leg of the 240V supply and neutral. In that case, obviously, without neutral those controls don't run.

keshlam
  • 28,994
  • 5
  • 48
  • 98
2

I have a 240v 30amp welder wired in the way you described. Hot, Hot, Ground.

Be sure to use the correct 2 pole breaker.

rpmerf
  • 336
  • 1
  • 5
  • Great, it finally worked. I also was not using a two-pole breaker, so dumb. My AC is now humming. – MANY Jun 23 '15 at 14:40
1

That's correct. If you're installing a 240 volt load, there's no need for the grounded (neutral) conductor. As you suggest, you will need a grounding conductor though.

Michael Karas
  • 64,542
  • 7
  • 63
  • 144
Tester101
  • 131,561
  • 78
  • 320
  • 610