I have a 200amp, 40 position but only can land 20 neutrals and 20 grounds because there aren't enough screws on the bar. I can't have 2 neutrals under the same screw. I do not have any empty spaces on neutral bus but have several double up neutrals. Can I add another neutral bus?
-
Is your panel a newer plug-on-neutral model by any chance? – Nate S. Apr 05 '21 at 18:13
-
What make and model is your panel? Can you post photos of the labeling on the inside of the panel's door please, for that matter? – ThreePhaseEel Apr 05 '21 at 22:45
2 Answers
You CANNOT add a neutral bus. You can add a ground bus.
Neutral is not ground.
The essential difference here is that neutrals handle normal service current 24x7... whereas grounds only handle current during a ground-fault event. So the neutral bars have thermal considerations ground bars do not, as well as, you don't want current to normally be present on the panel chassis, which is grounded.
So you cannot add additional neutral bars, but they provided enough neutral slots for your needs, so you are all set.
You can either add additional ground bars, or use the existing spaces as effectively as you are allowed to. See below.
UL would never have approved what you claim.
Are you sure you have a 40-position panel? If you have a 20-space panel, that does not mean you have 40 positions; some spaces are surely forbidden for tandem/double-stuff breakers if they only gave you 40 neutrals. You must heed those restrictions and not cheat around them.
In order to be approved by UL, a panel designed for n circuits MUST provide n neutral bar screw lugs, and also n / 3 (rounding up) ground screw lugs. That is because NEC and UL both require each neutral be entirely solo on its screw... but up to 3 grounds can share 1 screw provided the panel labeling allows this, which it usually does.
Typically, on cheapie panels, they provide only neutral bars, and simply provide extra screws (1/3) on the neutral bars for the grounds, on the assumption this is a main panel. If it's a subpanel, you are expected to purchase accessory ground bars ($4-7).
I do not believe for a New York minute that a 40-circuit panel shipped with 40 neutral screws only and no grounds.
That leaves only 2 possibilities: The original installer squandered the screws by wiring many grounds solo... and you'll need to triple up the grounds (or otherwise follow label instructions) so that have enough screws to solo the neutrals.
Or, the panel has been illegally double-stuffed (e.g. using non-CTL breakers in a CTL panel) and it has more circuits in it than it can support. That will need to be corrected, may be time to think about a subpanel.
Read the instructions carefully on accessory ground bars
Some of them do not allow 3 grounds per screw terminal, some only allow 2 or even 1.
However you must "stay within brand" of the ground bars; the panel labeling will specify specific models of ground bar, and they will bolt right up to the sites already drilled and notched for those bars. Easy peasy. You could use a 3rd party bar with AHJ approval, but it'd be an awful lot of work to drill and tap custom mounting holes for it. Not worth it for the $1-2 you'd save at most.
- 300,628
- 26
- 286
- 734
-
The one way I could see UL allowing this is if it's a plug-on-neutral panel, and the labeling requires a certain number of breakers to be of that type -- that way, the neutral lugs come with the breakers. Otherwise, most PoN panels would have a massive neutral bar with typically only a handful of wires on it, since no one pays extra for PoN only to use mostly standard breakers. – Nate S. Apr 05 '21 at 18:23
-
@NateS. That wouldn't work since only GFCI and AFCI actually use plug-on neutral (ignoring Leviton for this discussion). It would be the equivalent of telling the owner "you must fit a minimum number of xFCI breakers in this panel". That is also why most makes have the PON bar also have screws on it, so it can be used both ways. – Harper - Reinstate Monica Apr 05 '21 at 18:39
-
True, but for residential meter-main type panels anywhere that's using the 2020 code, it would work fine. Nearly every 120V circuit requires one or both of GFCI or AFCI, and many of the 240V circuits won't use neutral at all. For new construction, the range and dryer neutrals can actually be the only things that end up using the neutral bar screws. Moreover, there's nothing stopping any of the manufacturers from making a PoN regular breaker. I think only Leviton does so far, but if PoN gets very popular, others might follow suit. – Nate S. Apr 05 '21 at 19:23
-
I've seen at least one querent show up with a PoN QO LC that couldn't accommodate all the neutrals for its stated circuit count (on QO, thankfully, that's not the end of the world, as QONKx add-on neutral kits are a thing for QO LCs) – ThreePhaseEel Apr 05 '21 at 22:46
Yes, Best practice is to land all the neutrals on the same bus bar that's connected to your service neutral. If you need an additional bus bar, that's an easy connection, just use a large gauge wire (such as 4ga) between the added bus bar and the current one. You don't mention ground wires, but if you added a bus bar, it might be possible to move the current grounds to the new bus bar, bonded to the panel and the existing neutral bus bar. Pictures of the innards of your panel would help us give you better advice.
- 23,214
- 3
- 40