4

When connecting wires to the screw terminals on receptacles or light switches, what torque should they be tightened to if no torque is indicated either on the device itself or in its installation instructions? For example, the instructions for Leviton's receptacles and switches just say to "firmly" tighten them.

1 Answers1

6

Generally, 14 inch-pounds is safe, although you can go somewhat higher if you wish

UL 498 (i.e the standard for receptacles in the US) calls out a tightening torque of 12-14 inch-pounds for wire binding screws (depending on size) in Table 123.3 as part of the Terminal Strength Test, and repeats that 14 inch-pound figure for 12AWG wire in 113.13 for the Terminal Temperature Test. Given that you're generally dealing with duplex receptacles, and those almost always support through-wiring, 14 inch-pounds is a reasonable figure as 113.4 requires their terminals to be temperature tested with 12AWG wire if they aren't based on a 20A design, and most are based on a 20A design anyway.

Likewise, UL 20's terminal retention tests (found in clause 5.30) repeat those figures in Table 16, and Leviton's own specifications for their residential receptacles call out 14-18 inch-pounds of torque.

ThreePhaseEel
  • 83,293
  • 29
  • 137