I have a solar array on my rv and have installed a power bright 6000-12 inverter which I wired the rv supply line directly into the lugs on the front panel. I am having a problem with the inverter faulting. I checked the four receptacles on the inverter and they all show as n open ground the inverter has a chassis ground wire installed and the each sets of cables are connected to three 12 volt 180 amp/hour batteries wired in parallel and a solar panel with 30 amp charge controler. There are two of these panel/battery setups one on each pair of cables. The inverter turns on and faults after about a minute disconnecting the 120 ac power. Can someone please help me to resolve this issue? I am gong to add chassis grounds to that battery banks in the meantime while waiting for some replies.

longneck
  • 21,248
  • 4
  • 48
  • 79
  • 2
    Can you draw a picture of the way things are wired up? And when you say the inverter faults, does it tell you what the fault is? – longneck Sep 23 '20 at 23:33

1 Answers1

1

In the manual they discuss "battery bank" singular. As in one battery bank.

From a Home Depot review:

Installation tip: This unit has 4 battery terminals and all four terminals should have a dedicated minimum zero gauge cable and all 4 cables must connect to the same battery even if multiple batteries are present.

So this means that the 2 + terminals and 2 - terminals are not intended to support dual battery banks. They are intended to parallel the DC wiring side, due to the very large startup current needed (1000A when starting a large load).

Harper - Reinstate Monica